Pls assist in determining cable size (pvc armoured 4-core) for;
1. 400kw/415v panel distance from mains power panel -100mts
2. 120kw/415v panel distance from mains power panel-120mts

darkwood
29th July 2009, 11:38 PM
Its like asking you to book me an holiday that i will like their are so many parameters you need to know before i could possibly tell you:-
Ambient temp'

installation methods

Characteristics of load (Is it large inductive)

Is the Kw value you give balanced over 3 phase or per phase

These are just a few things to address but the list goes on prob best getting someone on site to assess as this size load may need parallel supplies per panel.

Besoeker
2nd August 2009, 05:04 PM
Its like asking you to book me an holiday that i will like their are so many parameters you need to know before i could possibly tell you:-
Ambient temp'

installation methods

Characteristics of load (Is it large inductive)

Is the Kw value you give balanced over 3 phase or per phase
Location, applicable standards, local regulations, etc.
In any case, this particular forum is to quote "For electricians and those already in the electrical industry. "
I would expect an electrician to have access to and be able to consult the appropriate tables in BS7671 or whatever equivalent standard is applicable.