Hi there , trying to find on the web the CRIPPLE sequence for testing but having no luck.
Could sombody please tell me the steps or send me a link were i could view them in full ?
Any help much appreciated.
Thanks
Steven
-
25th March 2010, 11:13 AM #2
Junior Member
- Join Date
- Mar 2010
- Posts
- 3
Re: CRIPPLE testing sequence.
C. continuity of earths including main and suplimentry bonding.
R. continuity of ring final circuit.
I. insulation resistance.
P. polarity
* the next ones are the live tests.
P. polarity of tails
L. loop impedance.
E. earth fault loop & earth spike (if its a tt)
R. rcd functional tests.Last edited by Howie; 25th March 2010 at 12:45 PM.
-
15th May 2010, 03:05 PM #3
Junior Member
- Join Date
- Sep 2009
- Posts
- 6
Re: CRIPPLE testing sequence.
Continuity: method 1 , Metrhod 2
Ring Step 1, Step 2, Step 3
Insulation resistance 250 V, 500V, 1000V
Polarity Dead colour and position
Polarity Live with proper tester not Martindale plug
Loop Impedance tests, Ze, Zs, Pfcc, Pscc
Earth Electrode Test with spike or loop impedance tester
RCD tests 1 30Ma X !/2 test 2 30Ma @ 0", test 3 30Ma @180", test 4 150 ma @ 0", test 5 150 ma @180" test 6 Function of switching
-