advise on hob/oven connected load
Hi,
have just had a new hob installed and got an electrician to wire in power supply for it. separate feed to 32amp rcd, at the time i asked him about wiring in a new single built under oven he said it would just connect to the 13 amp socket as last one did.
I received new oven today and specs says it is 16 amp.
The total loads are 5.9 kW for the hob & 3.6kW for the oven, can they be connected to the 32 amp rcd, or do I need to have him rewire again to a higher rating?
-
25th July 2010, 01:29 PM #2
Junior Member
- Join Date
- Dec 2009
- Location
- Newton Abbot Devon UK
- Posts
- 7
Re: advise on hob/oven connected load
The total load =9.5kW so therefore 41.30Amp
You could leave the hob on 32A MCB but need additional 16A MCB for the oven
-
2nd August 2010, 02:36 AM #3
Junior Member
- Join Date
- Aug 2010
- Posts
- 2
Re: advise on hob/oven connected load
I am assuming the skt you would plug into is already there?
If so how it wired do you know if it is on a ring main?
If so do you know if all you skts in the house are on one ring or is the kitchen on its own?