Thread: non tripping trip
|
|
|
-
30th May 2008, 09:58 PM #1
Junior Member
- Join Date
- May 2008
- Posts
- 3
non tripping trip
hi i have just tested a fuse board that i fitted. The property has a TT system with a ze of 176 mohms and a pfc of 1.10ka yet on doing a trip test on the 30ma rcd it will not trip out on x1 or x5 ! I have changed the rcd for new to see if i had a faulty bit of kit but the new one didnt trip either just wondered if anyone had any ideas ?
-
31st May 2008, 07:09 PM #2
Junior Member
- Join Date
- May 2008
- Posts
- 3
Re: non tripping trip
sorry people it was a typing error it is ohms not mohms
-
2nd June 2008, 03:57 PM #3
Member
- Join Date
- Mar 2007
- Location
- Kent, UK
- Posts
- 95
Re: non tripping trip
Hi, does the meter trip on a normal TNS/TNCS system? Regards Jim
Never argue with an idiot , they will bring you down to their level and then beat you with experience
-
5th June 2008, 10:13 PM #4
Junior Member
- Join Date
- May 2008
- Posts
- 3
Re: non tripping trip
hi jim cheers for replying ! I have sourced the problem now it was a fault on a lighting circuit that for some unknown reason stopped the rcd tripping out on a trip test it is now behaving as it should and i am a happier man many thanks again mark !
-
7th June 2008, 10:30 AM #5
Junior Member
- Join Date
- Jun 2008
- Location
- Kent
- Posts
- 1
Re: non tripping trip
Mark, I know you have sorted it now but what was the actual problem? I can't think what fault on the lighting circuit would have stopped the rcd from tripping,
regards,
Dave.