Thread: non tripping trip

   
  1. #1

    Default non tripping trip

    hi i have just tested a fuse board that i fitted. The property has a TT system with a ze of 176 mohms and a pfc of 1.10ka yet on doing a trip test on the 30ma rcd it will not trip out on x1 or x5 ! I have changed the rcd for new to see if i had a faulty bit of kit but the new one didnt trip either just wondered if anyone had any ideas ?

  2. #2

    Default Re: non tripping trip

    sorry people it was a typing error it is ohms not mohms

  3. #3

    Default Re: non tripping trip

    Hi, does the meter trip on a normal TNS/TNCS system? Regards Jim
    Never argue with an idiot , they will bring you down to their level and then beat you with experience

  4. #4

    Default Re: non tripping trip

    hi jim cheers for replying ! I have sourced the problem now it was a fault on a lighting circuit that for some unknown reason stopped the rcd tripping out on a trip test it is now behaving as it should and i am a happier man many thanks again mark !

  5. #5

    Default Re: non tripping trip

    Mark, I know you have sorted it now but what was the actual problem? I can't think what fault on the lighting circuit would have stopped the rcd from tripping,
    regards,
    Dave.