Thread: TT installations Testing

   
  1. #1

    Default TT installations Testing

    Hi all, Returning to the electrical fray in order to reduce costs from property rentals / redevelopments.
    One of the properties I have and will require annual test / inspection is a TT system. When testing the installation would I have to test the spike separately or would a good Ze / Zs reading suffice?
    Wanted to know so I could budget for what testers required.
    Thanks

  2. #2

    Default Re: TT installations Testing

    In my opinion a loop impedance tester will do.

    An electrode resistance tester allows you to test the adequacy of an earyth rod during dead tests, which is what you want for new installations.
    In the case of periodic inspections you are testing an installation that is already live.
    Regards

  3. #3

    Default Re: TT installations Testing

    You will get your Ze from the spike (method 2) you cannot get a Ze from anywhere else, BS 7671 says 200ohms or less stable however if your a member of a scheme this value may alter. Stable is the important word. Regards Jimbo
    Never argue with an idiot , they will bring you down to their level and then beat you with experience

  4. Default Re: TT installations Testing

    The Fluke 1653, is an installation tester and will do your electrode test with the spike kit. A useful all round tester

  5. #5

    Default Re: TT installations Testing

    spot on jimbo, the only place you can get the ze from, is the spike.

    i met one of those idiots yesterday and i did not stand a chance.

  6. Default Re: TT installations Testing

    Although 200ohms is acceptable, it could become unstable so its better to try and achieve around 100.