Thread: Drop @ CU input under load
|
|
|
-
28th May 2009, 03:39 PM #1
Junior Member
- Join Date
- May 2009
- Posts
- 2
Drop @ CU input under load
odd problem - when the ring main loaded up (e.g 2kW kettle or similar), the L-N voltage coming into the CU drops to circa 170V.
Anyone ever seen something similar to this ? Right now I can only think it's a high Z issue on the supply side, or very soon after it before it reaches the main switch in the CU.
It's been going on for a long time however, so wherever those watts are going, they aren't enough to further degrade wherever it is.
-
28th May 2009, 04:46 PM #2
Junior Member
- Join Date
- May 2009
- Posts
- 2
Re: Drop @ CU input under load
problem solved - loose connection at the meter





Reply With Quote