Thread: Cable Sizing

   
  1. Default Cable Sizing

    Pls assist in determining cable size (pvc armoured 4-core) for;
    1. 400kw/415v panel distance from mains power panel -100mts
    2. 120kw/415v panel distance from mains power panel-120mts

  2. #2

    Default Re: Cable Sizing

    Its like asking you to book me an holiday that i will like their are so many parameters you need to know before i could possibly tell you:-
    Ambient temp'

    installation methods

    Characteristics of load (Is it large inductive)

    Is the Kw value you give balanced over 3 phase or per phase

    These are just a few things to address but the list goes on prob best getting someone on site to assess as this size load may need parallel supplies per panel.

  3. Default Re: Cable Sizing

    Quote Originally Posted by darkwood View Post
    Its like asking you to book me an holiday that i will like their are so many parameters you need to know before i could possibly tell you:-
    Ambient temp'

    installation methods

    Characteristics of load (Is it large inductive)

    Is the Kw value you give balanced over 3 phase or per phase
    Location, applicable standards, local regulations, etc.
    In any case, this particular forum is to quote "For electricians and those already in the electrical industry. "
    I would expect an electrician to have access to and be able to consult the appropriate tables in BS7671 or whatever equivalent standard is applicable.