  1. #1

    Default Emergency Lighting Circuits!!!

    Hi, can anyone help,
    Last edited by fantomcat_2k; 19th December 2010 at 11:05 PM.

  2. #2

    Default Re: Emergency Lighting Circuits!!!

    This would normlly be carried out by a spe******t but I would test as a lormal lighting ciruit. You will also need to run the lights from the batteries. For about 4 hours to ensure they all stay on for this long. If they are supplied from an invertor cabinet you will also want to measure the batteries on charge, on load and on load after the four hour test to ensure no unnacceptable drops in charge.

  3. #3

    Default Re: Emergency Lighting Circuits!!!

    spe******t

  4. #4

    Default Re: Emergency Lighting Circuits!!!

    I wouldn't worry too much like CJ said only additional check would be a function test, but you will find that out when your doing the dead tests.