Thread: 17th testing

   
  1. #1

    Default 17th testing

    does 17th Ed let you test insulation resistance at 250v ?

  2. #2

    Default Re: 17th testing

    Yes if you look at table 61 on page 158 of the big red book, and read down from 612.3 Insulation resistance, it lays out when you may need to test at 250 volts, for instance when 500volts could damage electronic euipment.

  3. #3

    Default Re: 17th testing

    cheers robbie,so i expect >99.9Mohms is ok to put on cert ?

  4. #4

    Default Re: 17th testing

    Quote Originally Posted by clive jackson View Post
    cheers robbie,so i expect >99.9Mohms is ok to put on cert ?
    hate to be pedantic, but......nah i love to be pedantic

    you dont expect >99.9Mohms!!!!

    if you did, then you would have to fail a reading of, say, 98Mohms, or 97Mohms

    you EXPECT >1 Mohms for a 230V circuit, you may get >99.9Mohms, and you may get 5 Mohms, and both would be a pass as per table 61

    incidentely, i use this reg on exisiting circuits, and test @250V as a matter of course - if it passes (especially L-N) then i crank it up to 500V - saves popping that aeriel booster running off the lighting circuit in the attic!

  5. #5

    Default Re: 17th testing

    Cive why don,t you pay an electricianto do a part p test for ypu?

    regards stormin

  6. #6

    Default Re: 17th testing

    Quote Originally Posted by ringworm29 View Post
    Cive why don,t you pay an electricianto do a part p test for ypu?

    regards stormin
    ???????????????