17th testing
does 17th Ed let you test insulation resistance at 250v ?
-
14th September 2009, 03:05 PM #2
Junior Member
- Join Date
- Sep 2009
- Posts
- 21
Re: 17th testing
Yes if you look at table 61 on page 158 of the big red book, and read down from 612.3 Insulation resistance, it lays out when you may need to test at 250 volts, for instance when 500volts could damage electronic euipment.
-
15th September 2009, 10:32 AM #3
Junior Member
- Join Date
- Jul 2009
- Posts
- 4
Re: 17th testing
cheers robbie,so i expect >99.9Mohms is ok to put on cert ?
-
15th September 2009, 10:11 PM #4
Senior Member
- Join Date
- Aug 2009
- Posts
- 122
Re: 17th testing
hate to be pedantic, but......nah i love to be pedantic

you dont expect >99.9Mohms!!!!
if you did, then you would have to fail a reading of, say, 98Mohms, or 97Mohms
you EXPECT >1 Mohms for a 230V circuit, you may get >99.9Mohms, and you may get 5 Mohms, and both would be a pass as per table 61
incidentely, i use this reg on exisiting circuits, and test @250V as a matter of course - if it passes (especially L-N) then i crank it up to 500V - saves popping that aeriel booster running off the lighting circuit in the attic!
-
17th September 2009, 07:13 PM #5
Junior Member
- Join Date
- May 2008
- Posts
- 10
Re: 17th testing
Cive why don,t you pay an electricianto do a part p test for ypu?
regards stormin
-
17th September 2009, 09:57 PM #6
Senior Member
- Join Date
- Aug 2009
- Posts
- 122